You are currently viewing our boards as a guest which gives you limited access to view most discussions and access our other features. By joining our free community you will have access to post topics, communicate privately with other members (PM), respond to polls, upload content and access many other special features. Registration is fast, simple and absolutely free so please, join our community today!

If you have any problems with the registration process or your account login, please contact contact us.
Reply
 
LinkBack Thread Tools Display Modes
  #1 (permalink)  
Old March 26th, 2008, 07:16 AM
87 WE2's Avatar
BUICK TURBO PERFORMANCE
 
Join Date: Jun 2002
Location: Phily Area, PA
Trader Rating: (3)
Posts: 1,295
A few code?'s for an Electrician, more power to garage.

I have a 200amp service and want to extend more power to the garage. Right now I only have a 120v 15amp circuit out there.

I have a 60amp breaker to install in my house (Cutler Hammer) panel to feed my Sqaure D sub panel to go in the garage. My sub panel is a back feed through breaker style (I forget the technical term) I have a 60 amp breaker for it also.

My question's are:
What size conduit do I need to run for (3) #8 wires and (1) #10awg ground, (total distance of run 40ft garage to house)?

Are those wire sizes correct for my application?

I have to be 18" deep for conduit burial correct?

When I get into the house, do I need to still be in conduit all the way to the panel, or can I run regular copper #8 wire like for an electric stove?

If I do not have to be in the conduit in house (basement) can I splice the stove style wire into an LB that would be on the conduit comming from the garage, or is that a no, no?

Thanks very much for the help.
__________________
Mid Atlantic Grand National Association MagnaBuick.Com

87 GRAND NATIONAL:
86 T-TYPE: Light Chestnut Met. Sold

Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
  #2 (permalink)  
Old March 26th, 2008, 08:20 AM
TexasT's Avatar
Texas, Where are you from
 
Join Date: Sep 2002
Location: Midland
Trader Rating: (0)
Posts: 681
I'm sure a real electrician will know more and should post.

A lot depends on your local ahj and the edition of the NEC they follow. I used direct burial cable to avoid running conduit all the way. Any where it is exposed (going in and out of the ground and into the structure) should be put in conduit to avoid damage to it.

As far as exposed wiring within the structure, I believe if it is a certain height above the walking surface it can be left exposed when using romex. If it will be in the wall and is sheathed that will make a difference. Depends on the type of wire you are using.

I do know you should separate the neutral and ground in the sub-panel. There should be a removable bar there where the ground bus is.
__________________
Rich

1970 GS455
1987 WE4

Why doesn't "Buick" ryhme with "Quick"?
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
  #3 (permalink)  
Old March 26th, 2008, 08:31 AM
Danster's Avatar
Senior Member
 
Join Date: Nov 2001
Location: Plano, TX.
Trader Rating: (0)
Posts: 1,016
Post your question here. DoItYourself.com Community Forums - Home Improvement & Home Repair Questions & Answers

Went to this site to ask about adding a 220V source for my Air Compressor. Bunch of guys will steer you straight on what needs to be done.

Dannyo
__________________
87 Turbo T - TA49, Walbro 340, adj fpr, RJC Power Plate, ScanMaster2, MSD 50's, Trans +, LT1 MAF, extender chip, RJC FM Intercooler, 3" THDP & Big Mouth cold air kit, 3200 Stall Precision Converter.

Fastest ET 1/4 mile - 11.50 at 114 MPH
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
  #4 (permalink)  
Old March 26th, 2008, 08:43 AM
GregInAtl's Avatar
Senior Member
 
Join Date: Oct 2005
Location: Loganville GA
Trader Rating: (0)
Posts: 957
Quote:
Originally Posted by Grand Nash View Post
I have a 200amp service and want to extend more power to the garage. Right now I only have a 120v 15amp circuit out there.

I have a 60amp breaker to install in my house (Cutler Hammer) panel to feed my Sqaure D sub panel to go in the garage. My sub panel is a back feed through breaker style (I forget the technical term) I have a 60 amp breaker for it also.

My question's are:
What size conduit do I need to run for (3) #8 wires and (1) #10awg ground, (total distance of run 40ft garage to house)?

Are those wire sizes correct for my application?

I have to be 18" deep for conduit burial correct?

When I get into the house, do I need to still be in conduit all the way to the panel, or can I run regular copper #8 wire like for an electric stove?

If I do not have to be in the conduit in house (basement) can I splice the stove style wire into an LB that would be on the conduit comming from the garage, or is that a no, no?

Thanks very much for the help.
OK, every state is different, and sometimes county to county is differents. What we would do in the situation is;

I'd get direct burial, go 18" deep and and call it a day. Run from the sub panel to its own ground rod the ground wire and save some $ on that copper. just put it outside the sub panel in next to the foundation.
Splices are generallly a no-no nless they are junctioned and always accessable (But must be fully enclosed including a blank plate over them)
I'd do the 8 from the panel out to the garage one run, all "UF" or underground direct burial wire.
HTH
GC
__________________
Greg
86 GN hardtop - TE44 / THDP / 42#ers / Adj FPR / Hotwire / Walbro / 2.5" exhaust/ lots more parts to be installed....
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
  #5 (permalink)  
Old March 26th, 2008, 11:15 AM
87 WE2's Avatar
BUICK TURBO PERFORMANCE
 
Join Date: Jun 2002
Location: Phily Area, PA
Trader Rating: (3)
Posts: 1,295
I should have stated that the conduit and #8 wire feeds and the sub panel were all free. Left over material from a job at work, and my boss gave me the sub panel & breakers removed from panel upgrade job.

So basically I only need buy like 15' of wire in the basement
__________________
Mid Atlantic Grand National Association MagnaBuick.Com

87 GRAND NATIONAL:
86 T-TYPE: Light Chestnut Met. Sold

Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
  #6 (permalink)  
Old March 26th, 2008, 03:02 PM
Senior Member
 
Join Date: May 2001
Location: Fort Lee, NJ
Trader Rating: (3)
Posts: 1,659
Quote:
Originally Posted by Grand Nash View Post
I have a 200amp service and want to extend more power to the garage. Right now I only have a 120v 15amp circuit out there.
No, problem. Been doing electrical work for 18 years and licensed for the past 12 years of the 18. Should know something

Quote:
Originally Posted by Grand Nash View Post
I have a 60amp breaker to install in my house (Cutler Hammer) panel to feed my Sqaure D sub panel to go in the garage. My sub panel is a back feed through breaker style (I forget the technical term) I have a 60 amp breaker for it also.
Put the 60A breaker in your main panel. Run 6/3 Romex or BX (as per NEC) out of the panel to your exit location of the basement for the conduit. The mininum size conduit is 3/4. I run 1" or 1 1/4" for possible ungrade (welders, refriges, lifts, heaters, etc,etc) in the future. You don't need a breaker in the sub panel in the garage. The wires could terminate on the lugs in the panel.

My question's are:
Quote:
Originally Posted by Grand Nash View Post
What size conduit do I need to run for (3) #8 wires and (1) #10awg ground, (total distance of run 40ft garage to house)?
Run (3) #6 wires instead of the #8s. The #10 green (ground) is fine. The #6 wire is good for 60A.

Quote:
Originally Posted by Grand Nash View Post
Are those wire sizes correct for my application?
See above

Quote:
Originally Posted by Grand Nash View Post
I have to be 18" deep for conduit burial correct?
Yes. Use PVC, the gray stuff not the white plumbing PVC. Make sure you PVC cleaner prior to glueing the PVC.

Quote:
Originally Posted by Grand Nash View Post
When I get into the house, do I need to still be in conduit all the way to the panel, or can I run regular copper #8 wire like for an electric stove?
No. I don't know how old your house is. If it's old, the stove might be wired with 2 hot legs, 1 ground and NO neutral. This way is a code violation today.

Quote:
Originally Posted by Grand Nash View Post
If I do not have to be in the conduit in house (basement) can I splice the stove style wire into an LB that would be on the conduit comming from the garage, or is that a no, no?
I would run the either the RX or BX to your exit location and box it. Run your conduit into the box. This box is your conversion from RX/BX to individual conductors (THHN) that ran inside the conduit. Don't splice in the LB, although it's allowed provided you have the room, it's better to splice in a box.

Quote:
Originally Posted by Grand Nash View Post
Thanks very much for the help.
No problem

If part of the basement is above the ground, try to drill through foundation or wooden floor joist. Don't drill out under the ground, it's a pain to seal it or it will leak water into your basement.

Post a pic of your proposed work site and I be of assistance to your conduit run.

Do NOT use UF (underground feeder) cable. It is low budget and will burn up over time. UF wire keeps me busy at condo/townhouse developments, it keeps burning up or the landscaper chops it.

If you have any other question, just ask.

Billy T.
gnxtc2@aol.com
__________________
1987 GN "under major transformation"

Pictures

Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
  #7 (permalink)  
Old March 26th, 2008, 03:15 PM
87 WE2's Avatar
BUICK TURBO PERFORMANCE
 
Join Date: Jun 2002
Location: Phily Area, PA
Trader Rating: (3)
Posts: 1,295
Thanks I should have called the stove cable romex. Just bought some to hook up my new stove its #8 3 wire with a ground. Had that laying there so thats what I was thinking in my head. I'll get some RX or BX to get as suggested for the basement.

I think the panel I have did't have a main, no lug thats why I believe I needed the breaker to back feed the main into the sub panel.

Should I isolate the gound bar in the sub panel?

Conduit run is a piece of cake, straight out like 30' then a left turn 10' to the garage. Already have the gray pvc and glue, primer. I had #8 wire from work that was free, guess I'll buy #6. I plan to run a Dayton G73 heater with is 20.8amp on high. I have a 15 amp compressor out there. Probably will have a welding machine at some point. + my lighting 8 amps or so. I will obviously not be running all that crap at once but its better to have more power then you need then not enough

I am definatly going in above grade through the joist already made that desision.
__________________
Mid Atlantic Grand National Association MagnaBuick.Com

87 GRAND NATIONAL:
86 T-TYPE: Light Chestnut Met. Sold

Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
  #8 (permalink)  
Old March 26th, 2008, 04:16 PM
Senior Member
 
Join Date: May 2001
Location: Fort Lee, NJ
Trader Rating: (3)
Posts: 1,659
[quote=Grand Nash;1825433]
I think the panel I have did't have a main, no lug thats why I believe I needed the breaker to back feed the main into the sub panel. [?QUOTE]

Ah, no problem with backfeeding a breaker. I highly recommend that if you are backfeeding a breaker, the panel manufacturer makes a part that converts the breaker to be non-removable by ordinary means (can't be popped out).

Quote:
Originally Posted by Grand Nash View Post
Should I isolate the gound bar in the sub panel?
The ground bar should not be isolated. You can not put the grounds with neutrals on the neutral bar. The grounds and nuetrals must be kept seperate.

Quote:
Originally Posted by Grand Nash View Post
Conduit run is a piece of cake, straight out like 30' then a left turn 10' to the garage. Already have the gray pvc and glue, primer. I had #8 wire from work that was free, guess I'll buy #6. I plan to run a Dayton G73 heater with is 20.8amp on high. I have a 15 amp compressor out there. Probably will have a welding machine at some point. + my lighting 8 amps or so. I will obviously not be running all that crap at once but its better to have more power then you need then not enough
You never know when you could welding and the sparks ignite a small fire and you use the air blower to put it out

Billy T.
gnxtc2@aol.com
__________________
1987 GN "under major transformation"

Pictures

Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Reply



Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
Is there an electrician in the house? The Blob Turbo Lounge 14 November 28th, 2007 07:55 PM
Power 6 painting in my garage DougsfastZ Turbo Lounge 8 July 20th, 2006 11:35 AM
Electrician Help y26 Turbo Lounge 6 May 12th, 2005 10:35 PM
How do I become a Union Electrician??? V6UnderPressure Turbo Lounge 9 March 22nd, 2004 05:51 PM
New found power broke the tranny in the garage of all places Intercooler Turbo Lounge 23 April 24th, 2003 10:47 AM


All times are GMT -5. The time now is 10:36 PM.

Powered by vBulletin Version 3.6.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
Content Relevant URLs by vBSEO 3.1.0
One of the largest message boards on the web !